Author Topic: Transfer switch not locking into Short Power mode reliably  (Read 6736 times)

Greg Ross

  • BAC Member
  • *
  • Posts: 46
  • Thanked: 16 times
Re: Transfer switch not locking into Short Power mode reliably
« Reply #30 on: July 22, 2023, 05:25:48 AM »
Just a note, #12 wire is good for only 16 amps continous, the 20 amps is for short time only.
2008 Contessa
C9 425HP

Steve Huber Co-Admin

  • Administrator Group
  • *
  • Posts: 3516
  • Thanked: 2704 times
Re: Transfer switch not locking into Short Power mode reliably
« Reply #31 on: July 22, 2023, 04:33:21 PM »
Richard,
You might want to try cleaning the transfer switch contacts. I they are dirty/corroded they can cause a resistive contact that will build up heat.
Steve
Steve
2015-          07 Contessa Bayshore C9,  400 hp
2013-2015: 00 Marquis Tourmaline, C12, 425 hp
2005-2013: 01 Contessa Naples, 3126B, 330 hp

Bill Lampkin

  • BAC Member
  • *
  • Posts: 1233
  • Thanked: 359 times
Re: Transfer switch not locking into Short Power mode reliably
« Reply #32 on: July 23, 2023, 03:52:51 PM »
Can't tell you why, just what worked for me. No problem since removing temp sensor.
2005 Patriot Thunder Lexington, 3 slides
40' tag axle (short wheelbase)
525 hp C13

"Goin where the weather suits my clothes..."

Richard Davis

  • BAC Member
  • *
  • Posts: 213
  • Thanked: 86 times
Re: Transfer switch not locking into Short Power mode reliably
« Reply #33 on: August 17, 2023, 09:47:22 PM »
Thanks to all who have responded with suggestions.  I have finally resolved my issues.  I removed, disassembled and cleaned the 40250 ATS.  After reassembly, things were better except the ATS was still dropping contact when on generator with a load of over 20 amps.  I tested the generator output under load and found that voltage was dropping below 100 volts.  The 40250 ATS is designed to drop out if voltage drops below 105 volts, so it was doing what it is supposed to do.  I ordered and replaced the circuit breaker on my Onan QD8000.  Now everything is happy and functions as it should.  If anyone is in need of a 35 amp two pole circuit breaker that Onan used on the 7.5 and 8K generators, I found it on Amazon from the OEM manufacturer (AIRPAX, IEG66-28333-2-V) for about 2/3 of what Cummins wanted for it.
All's good that ends well.
Richard

06 Monterey Ventura IV, C9 400 hp
The following users thanked this post: Joel Ashley

Joel Ashley

  • BAC Member
  • *
  • Posts: 2348
  • Thanked: 805 times
  • OSU Class of '73, Oregon Native. RVing 39 years
Re: Transfer switch not locking into Short Power mode reliably
« Reply #34 on: August 18, 2023, 06:36:16 AM »
 ;)

So many times the transfer switch is suspect due to symptoms, but turns out to be doing the job as designed, and the primary issue is elsewhere.