Seems like Bruce, since he had it apart to replace the GFCI and had wires in hand, could simply measure the size of the wires with a common wire-crimping plier tool, and conclude what amp circuit is involved. The 15 amp rating of the outlet could come from it being a previous owner's handy but not exact replacement. If anyone has a diagram book for an '03 Marquis, that may indicate his appropriate amp rating for that and downstream outlets as well.
The thing is though, he indicated his breaker was 30 amp. That seems more like the Inverter Main incoming line than the individual circuits out of that box, and he's not looking at the right breaker. I'd expect the circuit in question (at least one bedroom outlet plus others downstream) to be 20 amp. The only 15 out of our 30 amp Main, for example, is the one for the two bath areas; the rest are 20's. 20 amp implies size 12 wire, whereas 15 amp is the smaller 14.
If Bruce's actual breaker is a 30, or even the 20 I suspect the correct one really is, that 15 amp-rated GFCI could be deemed a hazard; it could conceivably heat up under heavy load before its upstream breaker flipped off.
Forgive my assumptiveness, as a Marquis may be different in some wiring configurations than our Monty.
-Joel