Author Topic: exercising Onan generator  (Read 2471 times)

Don Melnechenko

  • Guest
exercising Onan generator
« on: September 26, 2016, 08:12:38 PM »
Is it necessary to unhook the shore power before starting my Onan 7.5 diesel generator when exercising it? 

Don Melnechenko
2003 Beaver Baron 34 ft.

Gerald Farris

  • Guest
Re: exercising Onan generator
« Reply #1 on: September 26, 2016, 08:51:30 PM »
Don,
No, it is not necessary to unhook from shore power to exercise your generator. Your transfer switch is designed as a generator priority device. So, if it detects power from both sources at the same time, it gives the generator priority and connects the coach to only the generator and disconnects all shore power from the coach.

Gerald