Keith and Carol,
Our Monterey was certainly different than your coach. However, it had a habit of mysteriously tripping the breaker on the genset. Maybe yours is similar.
The answer turned out to be the Inverter/Battery charger. On ours, the genset CB was a double 30 amp. If the cleverly smart battery charger sensed that the batteries needed a charge it would immediately go to work at maximum effort drawing a lot of amps briefly. So, if anything else with any significant load (like an air conditioner or the HydroHot) was on, one of the two 30 amp circuits would be briefly overloaded and the cause the breaker to trip.
In other words, it did not work like one big 60 amp/7500 watt genset. It worked like a pair of 30 amp/3750 watt generators where each could shut down everything if one saw a brief overload.
Have fun in AZ! We should be following you. The Puget Sound region weather suck!
Bill