Tom,
I am not near as good as Ed with electrical issues, but I think that Magnum requires a subpanel after the inverter to protect the circuits after the inverter. With the only breaker in the inverter circuit being the 30 amp inverter input, the circuits after the inverter are unprotected from a short circuit when inverting. This creates a shock hazard as well as a fire hazard.
Most Xantrex inverters have a breaker on the inverter for each of the inverter outputs, but Magnum does not, so they require a subpanel to protect each circuit. However, if your inverter outputs run back to a breaker at the main panel area, you are good to go with the only unprotected wire being between the inverter and the breaker, but I doubt that your coach is wired that way.
Installing a subpanel is very easy. Just run a 10/2 with a ground or a 10/3 wire from the single Magnum output to a small two breaker box, with 20 amp breakers, that you mount next to the inverter and connect the two current inverter output wires to the breakers.
Gerald