I have the same genset. It provides 30 amps to each leg. Shore power provides 50 amps to each leg. So, there is a 40% reduction in power available. You could even say that the genset provides "about half" of what shore power provides. Because of the way it is wired it can be thought of as two separate 3600 watt generators. The circuit breaker limits don't even allow the full 7500 watts the the label says it will do.
Other than my ear, i have no way to tell what the RPM is. So, in other words, the only measure of RPM is "loudness", which changes as the load changes. But, I do have voltage and amp readings in the Aladdin system. So, normal operation is constant voltage and variable "loudness" as the amp load changes.
On my motorhome, it is easy to pop a breaker. The inverter/charger is set to take full advantage of a 30 amp supply when it senses that the batteries are low. The inverter/charger is on the same 30 amp leg as the front air and fridge. If the house batteries have been used or are discharged in any way, the inverter/charger will take most of the available 30 amps on that leg for several minutes. If anything else is on it will exceed the 30 amps, the genset will "surge" and the breaker does what it is supposed to. Leaving the fridge on automatic will cause it to switch to electric and be part of the problem. If the charger is working hard and I turn on the air it will blow the breaker too.
After several minutes, the amp load of the charger will drop and stabilize. Then I can run most of what I want, but not as much as when plugged into shore power.
Perhaps your surge and resulting breaker pop are a normal function caused by too much electrical load on one of your "legs'.