Post by: Brent Hohlweg on December 11, 2013, 06:19:07 AM
Hi guys,

Wondering why my 12.5 Onan Genrator may not be turning over:

1. 180hrs total use.
2. Been using it regularly without issue for last couple months as we dry camp.
2a. Oil shows full, coolant is full.
3. Last week we had a hard time getting it to start in the cold weather. I was able to only get it to start once I had also fired up our coach - produced a big cloud of smoke out the exhaust once it finally started.
4. Today after multiple attempts to start the generator - both with coach engine on and off, it would not turn over.
5. The generator seems to labor away trying to turn over, white smokes comes out...

Could it be that our Coach Group 31 batteries are dying and with recent cold weather there just is not enough cranking power... and by trying to start the generator multiple times (never cranking more than 30secs and waiting 2 mins between attempts like the manual says) we have some how damaged the alternator ?

Any ideas would be totally welcome :-)

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Robert Mathis on December 11, 2013, 01:05:16 PM
When you saw it won't turn over, do you mean nothing happens when you hit the switch, or that it turns and just never fires? If it doesn't actually turn over when the switch is pressed, you either have a battery problem or the starter or solenoid is bad. The described symtoms of hard start coupled with heavy white smoke would indicate a problem with injectors or fuel flow. Have you changed you fuel filter lately? How cold is it where you are? Are you using the battery boost (parellel) switch when trying to start it?
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 11, 2013, 04:43:52 PM
Hi Robert,

Thanks for the reply :-)

Sorry what I meant is that it gets power when I'm pressing the gen start button. However the gen just cranks like when you have a dead battery in a car and the alternator just can't get the car started. While I'm pressing the gen start button we can see white smoke keep puffing out the tail pipe.

We have have not changed the fuel filter. I also wondered if it maybe it got some dirty diesel in it and it's clogged up... But the Cat12 main engine had had no problem.

It is cold here now (Scottsdale Arizona and now City of Rocks State Park in New Mexico)... Both getting down to about 26-27F overnight.

But yesterday I drove 4hrs to this State Park in New Mexico and arrived around 4pm and tried to start generator and we could not get it to start (as described above)...it's been just over the last couple weeks it seems to have started having these issues. We've been able to eventually get it to start (with a giant huge white/blueish cloud of smoke - like what happens when a car backfires).

PS: Funny you mention the "start booster"...Two days ago I tried that and was able to get it to work (but it created that giant cloud of smoke). That is also partly what made me wonder if the Group 31 batteries were dying)?

** How often should the fuel filter be replaced?

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Tom and Pam Brown on December 11, 2013, 05:52:03 PM
Brent,

If you depress the switch in the opposite direction it primes the fuel and gives the glow plugs a chance to work longer.

Next time you try it mash the other side of the switch for a little longer time say a minute or so and then try to start it.
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 11, 2013, 06:28:57 PM
Hi Tom,

Thanks for your reply!  Yes I've been following the manual and doing up to 60seconds priming holding down the opposite direction of the gen start button... but alas even doing that plus using start boost while plugged in to 50amp power has still not allowed me to get the gen to fully turn on... It just cranks away like a car with a dead battery / alternator that cannot fully start (it's just puffing white smoke out the side while I'm holding down the gen start button).

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Gerald Farris on December 11, 2013, 07:53:11 PM
Brent,
If your coach engine starts OK, the group 31 chassis batteries are OK. There is a possibility that the fuel filter for the generator is clogged, but it is a very remote possibility from your description. From your description of the problem, it sounds like you need to see a qualified Onan technician for the necessary repairs, unless you feel qualified to trouble shoot a diesel fuel system.

Gerald
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 12, 2013, 04:29:33 AM
Ok guys I made an appointment for tomorrow at Cummins Rocky Mountain in El Paso, TX to have them take a look.

**If anyone has any knowledge on what best to hace them service if I'm already paying them to look at this issue that would be great :-)

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Edward Buker on December 12, 2013, 04:41:04 AM
Brent,

It should be that you have good batteries if it starts the C12. That is especially true if the C12 cranking seems to have normal cranking speed and is  not laboring to start. If that is the case you can assume the batteries are fine but you may still have a resistive connection between the batteries and the genset. That can be at a battery terminal, a stud type terminal where two wires of the battery harness going to the genset join, or a ground to the coach frame that is rusted at the battery end or the genset end.

When you say it cranks away like a car with a dead battery, that implies slow cranking and low voltage at the genset to me. If the cranking is slow and not normal for your genset you need to check those connections and sort out what the voltage is at the genset end while cranking. If you are not getting over 10V then that may be the source of your issue. A slow cranking diesel will bring in fuel but not have enough heat generated to fire the mixture. White smoke will be emitted and when it does finally start you will have a lot of smoke being emitted by the unburned fuel.

You might also check that no animal has nested in the air intake system/filter housing.

If the genset cranking is as energetic as ever and it just does not start then I would head in the direction that Gerald sent you and get some service...

Later Ed
Title: Re: Onan Generator Won't Turn Over
Post by: LarryNCarolynShirk on December 12, 2013, 06:26:59 AM
Brent,

You may give this a try.  Hold down the start button for 3 seconds and let go.  Immediately, hold down the start button again.  Each time you push down the start button, the glo plugs heat up for a pre-established time and turn off.  That time may not be long enough for the cold weather you are experiencing.  The time period is about 3 seconds.  By heating the the glo plugs two or three times may be your answer.  It worked for me.  I learned this from a tech at the Onan dealer in Coberg, OR several years ago.  He discovered this short time-out on the glo plugs, when several coaches at a nearby rally experienced the same symptoms on a cold day.  It costs nothing to try.

Larry
Title: Re: Onan Generator Won't Turn Over
Post by: Robert Mathis on December 12, 2013, 01:03:44 PM
Please let us know what the problem turns out to be. It does sound like low voltage to the starter, but one never knows. The genset on my boat got a clogged injector one night about 2:00 A.M. and started running rough with tons of smoke. Fortunately, the clog cleared itself after a couple of minutes and all was well. Since we were 80 miles offshore at the time, I was a tad concerned. How often you should change the fuel filters is dependant on the quality of fuel you buy and the length of time in the tank. We changed fuel filters about every 200-300 hours on our boat, but carried several sets of spares. On the Onan in the coach, we change it once a year, without regard to hours. The filter is fairly cheap and good insurance to us.
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 14, 2013, 05:09:42 PM
UPDATE:

Took our coach into Cummins Rocky Mountain in El Paso. After a full service and the technician diagnosising it as "air getting into the diesel fuel line"...because once he drain the line and did a full service (fuel filter, oil filter, coolant change)...it started.

BUT!

I was not feeling that confident, so we drove to the near by Heuco Tanks State Park were the following morning it did not start again. So I went and replaced my two chassis batteries as they were near end of life and needed to be done at some point anyways. But today the gen never started again, after a 2min glo plug warm up again it would not turn over (it's like the generator is just not getting enough power to turn over and start).

SO:
The gen set read at Cummins as getting 12.6 volts while attempting to turn over and start. So could it be that with new batteries and full servicing the issue is... The gen set connections from the battery are all rusted up and dirty after almost 10yrs and we're just on the edge of getting enough power to turn over the generator. I'll go underneath today and clean them up and see how that goes.

PS: I'll keep everyone posted and also will upload a photo from the Cummins shop where a guy with a 06 Beaver Monterey was having his entire gen pulled out at a cost of over $2000 :-(
Title: Re: Onan Generator Won't Turn Over
Post by: Norm Green on December 14, 2013, 05:47:28 PM
My generator starts off the house batteries, not the chassis batteries.  Have you confirmed which batteries start the generator?
Title: Re: Onan Generator Won't Turn Over
Post by: Gerald Farris on December 14, 2013, 05:49:30 PM
Brent,
If your generator has 12.6V at the starter when it is cranking, low voltage is not the problem.

Gerald
Title: Re: Onan Generator Won't Turn Over
Post by: Dave Cunningham on December 14, 2013, 06:15:51 PM
Hi Brent, I have been following along here hoping I could offer some advise as I have had my share of generator issues, but the other guys seem to have covered all the basics, the main thing being ; getting over 10 volts to the unit on startup, I'm assuming that it does turn over ,but will not fire. Since you have just had it serviced , I would take it to a reputable onan shop and get them to diagnose again, and if it actually comes down to being a control board issue, it just occurred to me that I still have the one that I changed out of my last marquis, and I know that there is nothing wrong with it, when I bought the board I was told that the unit had to be removed from the coach to replace it , but that is not the case, it can be done with the genet slid all the way out.
The control boards for those 12.5 s are about $1100.00 so if you or anybody else reading this ever needs one I have it on the shelf.

Dave
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 14, 2013, 06:42:12 PM
Thanks for all the help guys!

I just fully cleaned the generator terminal connections and made them look brand new - nice and clean, but alas it still will not turn over. It just cranks and blows white smoke (seems dirty towards blue today - but that could be the couple attempts at starting the gen over last two days and it not successfully starting up).

I going back to Onan again and having them take a second review.
Title: Re: Onan Generator Won't Turn Over
Post by: Dwight Wilson on December 14, 2013, 06:45:03 PM
Just a thought but that blast of white smoke typically indicates unburned fuel in a cold start, Has anyone checked to see if the glow plug is functioning?
Dwight
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 14, 2013, 07:44:31 PM
So I'm going to throw this out there, as I dismissed the idea after the technician said he had never seen a glo plug fail...(see pics).

Plug #1 area is covered in oil. Could there be oil getting all over the glo plug somehow and gumming it up so that essentially all I'm getting is two good plugs to work? Maybe the plug just needs to be replaced.

Also here is a video of the gen failing to fully starting and the white smoke. Just click to download (link valid for 30days): https://www.dropbox.com/s/883c504tqrhd8v8/Video%2012-14-2013%2C%2011%2059%2030%20AM.mov

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Steve Huber Co-Admin on December 14, 2013, 08:20:36 PM
Brent,
White smoke is usually an indication of unburned fuel. Check the air filter and housing to be sure both are clean. Also, try starting the geni with the load disconnected (should be a circuit breaker on the geni). If it starts, let it run for 10-15 minutes to get rid of the unburned fuel in the exhaust system. The apply the load. If it continues to run, let it run for at least 15 minutes. As other have noted above, if it cranks with 12+ volts you don't have a battery problem.
Steve
Title: Re: Onan Generator Won't Turn Over
Post by: Edward Buker on December 15, 2013, 12:33:41 AM
Brent,

To get the terminology right, when you say it will not turn over, to us that means that the starter will not turn the crankshaft when the starter is engaged. Your case is that the starter engages and the genset turns over but it will not start. If it cranks over at good speed then low voltage at the starter and poor connections are not your problem. So as a symptom what you have is the genset cranks but will not start. So the first thing to have them check is that the system that powers on the glowplugs is working, the duration of glow plug on time is correct, and that the resistance of each glow plug is as it should be. If that is correct then the next system is fuel supply.

Later Ed
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 15, 2013, 01:03:07 AM
Ed, Gerald, Steve, Dwight, Dave and everyone who has posted on page 1...major thanks for all the extra info!

I started this process knowing nothing about my generator. As of now with this forum, tons of YouTube videos, Googling, and going to the Cummins shop I'll be able to do all my regular maintenance myself :-)

I'm returning to Cummins again on Monday and will post here the update.

Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 17, 2013, 06:24:00 PM
UPDATE:

At this point after 2 days of testing and stumping the technicians...Cummins has pulled the generator and it looks like it might be an electronic fuel pump. I'll post the final diagnosis. Thanks again everyone.

Cheers Brent
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 25, 2013, 06:18:52 PM
UPDATE (SAGA Cont):

These we're the items repaired - generator worked for 2 days and has now stopped working again and I'm reading Code 45 (four flashes - five flashes) coming up. We have no gen power on Christmas Day so the better half is less than impress :-(

Here is what Cummins diagnosed so far:

1. A sticking 'speed actuator' and replaced.
2. One defective glo plug and we replaced all three.
3. A 1-2mm crack in a hose (see above pics) that lead to area by glo plug #1.

We have left El Paso now, so we will have to hit another Cummins on the 27th in Lake Charles, LA.

I'll continue to keep posting in hopes that is helps others in the future.

PS: For all others having their generators pulled out... I just read another BAC post on generators and now see that Cummins should have replaced due to age "Replacing the temperature sender unit, belt, and thermostat..." http://forum.bacrallies.com/m-1387907037/s-new/#num2 (hope that also helps others).

Merry Christmas everyone,

Cheers Brent



Title: Re: Onan Generator Won't Turn Over
Post by: Edward Buker on December 26, 2013, 02:09:51 PM
Brent,

The thermostats rarely fail. The temp sensor can fail but not very often so that one is personal choice. If you are at a point in repairs where the belt is accessible and it is over 3 year old or shows any signs of wear or drying out then by all means change that out and save a future headache. This is my own opinion created from trouble shooting an overheat problem with my own genset. I had access to how many of each of these parts were sold each year from a Cummins/Onan parts manager (including water pumps which were almost never). He could do a national look from his computer terminal and from that you could see the real culprits by the number of part sales....

Later Ed
Title: Re: Onan Generator Won't Turn Over
Post by: David T. Richelderfer on December 26, 2013, 03:13:20 PM
Just a note:  While I was in the Challenger Automotive shop in Lake Havasu City late on Friday, December 20, 2013, discussing my Onan generator problem, Bill McVicker received another call from another motorhome/Onan owner with exactly the same error condition, e.g., temperature sensor fault.  The other owner was told the identical story as I had just received - come in Monday and we'll order the parts.  When the parts arrive, then we'll make a firm appointment to bring in the coach for a one-day in-and-out repair.

I remember Bill pointing out that the temperature sensor's and thermostat's longevity depends in large part on how often the engine's coolant is changed.  I have no idea when or if at all the thermostat and belt had been changed since the generator was manufactured.  My generator's S/N starts with J02....  That's a 2002 manufacture date - over ten years old.  So I elected to get 'er all done.

Except for the expense, this has been yet another great learning experience.  And $500 to $600 is relatively cheap after hearing about tow-jobs, alternator problems, leveling issues.  I just can't wait to change my eight tires... lots of zeros in that bill.
Title: Re: Onan Generator Won't Turn Over
Post by: Robert Mathis on December 27, 2013, 11:59:51 PM
David, I had to replace all 8 of my tires this spring, go with the Monaco International program if you can, it saved us a ton of money, like $200/tire. I'm like you, if my genset needed to have serious parts replaced, I'd go ahead and replace the belt, thermostat and coolant. I figure it's cheap insurance
Title: Re: Onan Generator Won't Turn Over
Post by: Brent Hohlweg on December 28, 2013, 04:55:21 PM
FINAL REPAIR UPDATE:

So we arrived at Cummins Mid South, New Orleans. The repair was covered under warranty for the work of El Paso Cummins shop - so no payment. They had a Onan generator specialist with over 15 years experience (Ronnie O.). Took him 30 minutes to diagnosis and work in reverse to find the problem of the Code 45 Speed Sense fault:

1. A loose and broken wire on the relay. Replaced and generator has been working great since.

Thanks again everyone. Hope this post and thread helps others in the future.