I would truly Appreciate help from you guys.
1. Installed 4 new house batteries and a new Victron MultiPlus 3000 Watt 12 Volt Inverter & 120 Amp. Additionally added Victron Energy VE.Bus Smart dongle, connects temperature sensor to positive terminal on house battery bank and uses a CAT5 cable back to Inverter to provide battery temperature for charging (Uses blue Tooth to provide simple info on battery status). EVERYTHING WORKED PERFECT for 1 YEAR.
2. TOOK 7 Day trip to Colorado Rockies, freezing cold weather, everything worked fine.
3. Returned home and plugged into shore power, Inverter stayed on Bulk Charge for 3 days for house batteries, would not cycle to Absorption mode.
4. Replaced 4 house batteries with new batteries. New batteries did not fix the problem, Inverter continued to stay on bulk charge.
5. Battery cables at Inverter connection show under 1 volt, with shore power disconnected then the inverter indicates LOW BATTERY and shuts off (does NOT start Inverting like it does when everything worked)
6. Battery cables at House Battery connection show 14 to 15 volts with Inverter in Bulk charge mode.
7. With shore power connected and Inverter/Charger on I have both DC power and have power through AC panel. If I shut off the Inverter I lose both AC and DC power. NOTE: Shore power runs directly to TRANSFER SWITCH(TS) and TS is wired directly to AC Panel, the AC panel provides a 20amp line to the INVERTER for pass through when on shore power.
8. Note: there is 2 long beeps I think from our fridge or somewhere in the ceiling, when I shut the Inverter off and then all AC shuts off, Air Condition Units, Fridge ETC. - The INVERTER is not wired between shore power and the AC panel so the loss of DC power is somehow involved.