Joel Ashley:
As some here know, due to one or either or both of us having medical issues, our coach has been parked by the house for nigh-on a decade.  I’ve had issues with varmints getting in the basement somehow and perching on the inverter (Magnum 2012) when it’s on, keeping the batteries up over winter.  They like the warmth apparently.  A few years ago I tried anti-rodent expanding foam under the coach where looms penetrated the rails through the tank bay that adjoins the main storage bay where the inverter mounts to the ceiling.  But I had to guess at where the loom hole was, and had a time seeing what I was doing under there, foam bits went everywhere, including on me;   I may have only somewhat mitigated the problem, not solved it, because I couldn’t get in a good viewing position.  And the critters are obviously undeterred, except by the inverter no longer being on and warm.

Well I got the inverter repaired that time, but for awhile now it’s again been out of commission.  The solar system keeps the batteries up, but the inverter wont turn on.  I assumed the worst when I saw old leaves and such in the wires next to the inverter today.  It was a bear to get off the ceiling and replace twice before.  And after 6 surgeries since 2025, I’m at 78 only now up for tackling getting in and out of tight environs for repairs.

Today I did preliminaries, cleaning out the detritus and such, and opted to do first things first, finding no voltage at the red DC input terminal of the unit.  My voltmeter sees nothing between the left side of the 300A fuse in the battery bay box and battery ground post, but 12+ volts on the right side.  So if I may thank the gods not to have to lift that inverter off the ceiling again (a fun project twice before!), am I on the right track simply replacing that Littlefuse JLLN 300?  I need a brain refresh, as I think I replaced that fuse once before. 

Crossing fingers that any long dissipated squirrel/chipmunk contaminant is no longer shorting internal wiring, and that I can find a permanent prevention?

Joel

Eric Maclean Co-Admin:
Joel
You are correct if that fuse is blown the inverter will not do anything.
The bigger question is why is that 300 amp fuse blown, it is possible that the inverter has an internal short.
Before installing a new fuse I would jump the old one with a booster cable momentarily and observe whether or not you get a large spark or ark.
This will tell you if the inverter has a significant draw or short.
It is possible that the fuse just died but I'd be weary.
Once you've changed the fuse I'd run the inverter through it's paces to verify proper operation paying attention to the amp draw on your RC50 control panel.

Eric

Steve Huber:
Joel,
I'd also consider switching to an external battery charger to keep the batteries up and turn off the inverter.
Steve

Joel Ashley:
Yes, I’ve a new charger that did the job when there wasn’t much solar input, although keeping the mains switched off limited parasitic battery drain.  One remaining question, is the proper fuse fast or slow-blow in this application.

Joel

Steve Huber:
Joel,
If you are referring to the 300A fuse, I'm pretty sure it's an ANL fuse and they don't come in slow blow.
Steve