Low voltage fuse box melt down
Jim Shunkwiler:
The damaged fuse box is located in bottom left corner of the big fuse box in the bathroom. The upper left corner has two wires in the same wire harness. They are labeled MOD DATA or HOD DATA. The seem to be what got the hottest. The lower left corner of the circuit board burned the most. One wire is black stripped the other is yellow with brown strip. Hope this helps.
Joel Ashley:
I'll try to remember to check the cabinet tomorrow, as what you describe has me scratching my head - can't picture a "big fuse box". Perhaps I'm totally forgetting one. Aside from the obvious 10 amp fuses in the two multiplex modules, the only others are in the flush mounted little black one with a snap off cover. The other two boxes are the standard 50 amp Main and the 30 amp inverter breaker boxes.
MOD could refer to Multiplex Output Data, or be a tag for output module dimmer, but that's a wild guess. Obviously, determining what it is will help clue you to what circuit and devices are involved or at fault.
Joel
Jim Shunkwiler:
Joel your description is correct. I'm talking about the House breaker/ fuse cabinet in the bathroom. The very bottom left corner. The two boxes at the bottom look the same.
Joel Ashley:
On the diagrams I attached previously, the second image, your culprit is the connection at J2 of Module A (10 CHANNEL OUTPUT MODULE DIMMER A), Jim. Intellitiec manufactures these Multiplex Output Data (MOD) modules, and it sounds like you'll need a new one. J2 on both modules A and B have only a white-striped brown and a red-striped yellow wire, tagged "MOD Data"; they are + and - data wires from the multiplex control, regardless, which splice to each multiplex switch throughout the coach.
As I understand Multiplex, and that's not very clearly, lighting is digitally managed - data sent to the controller on the above mentioned wires changes depending on how long a switch button is held, etc., and the two modules adjust dimming power to their respective lamps accordingly. The odd men out here are the two ceiling fans and the water pump, but they are on Module B. I would think the data circuit itself would use minimal amps, as opposed to the 10 amp lighting circuits they control, so it befuddles me (easily done) why your J2 connection would overheat. The multiplex controller itself I think is the "IPX CONTROL" in the diagram, and you can see it has its own red 10 amp fuse, which may be the one in position 9 on the inset 12v. house fuse block. Ed or Steve may understand this circuitry better, and can infer more from the diagrams and what you and I have written.
Before installing a new module A, I'd sure find out what caused the meltdown and why that controller fuse didn't blow to protect the data circuit. Did any of the switches get wet somehow? I know if I was anywhere near Bend I'd get in to have things analyzed by knowledgeable techs.
-Joel
click on the photo to enlarge it.
J2 is the white connector, nearest the fire extinguisher, on the circuitboard of Module A; they splice to the control, Com + and -, with the red wire supplying backlight power to the switches
Jim Shunkwiler:
Thanks so much for the help. Another interesting result after the incident is all the light switches are lit up and stay on.I wish I was near Bend but I'm in Houston and will be taking coach to local shop Monday. Do you think water in the the battery compartment could've caused this problem.