Mike,
The 120V AC amp requirement of the frig times 10 is a little low, maybe 12 would be right given there is efficiency loss within the inverter, some of the energy is consumed by heat created by the electronics. That being said that level of power (amps at 12v) is only required during the time the compressor is on, so assume that you run 20 minutes three times a night at 3.5 amps at 120v or one hour total as an example. That would be 12 times 3.5 amps or 42 amps for one hour which is 42 amp hours. While I believe in total you will consume more than that amount with defrost cycles, background electronics of the fridge and coach, you an see that you should have capacity for at least a night and part of a day if managed.
Later Ed