Technical Support / Re: Onan generator 7500
« Last post by Eric Maclean on April 21, 2024, 09:06:56 PM »Randy
How long has it been since you saw it run properly?
It may still be a fuel issue .you may still have air or a restriction.
The first thing I would do is turn off the breaker/s on the gen set and then let it run for an hour or more to warm it up well and see if it doesn't smooth out then turn the breaker back on and load it with about a 2k watt load to see how it responds.
Eric