Well I just received my new front AC roof unit today. In the process of taking the old one off, I noticed the four anchor bolts holding it on to the roof were very loose. If fact, I was able to turn a couple by hand and the other two took little effort to turn with a wrench. So.... when I put the new AC on the roof, how tight are those bolts supposed to be?
-
check the instructions from Dometic. Something like 22 in lb. Does your rig have the drain pans to drain the A/C condensate overboard? If so, you should use two new foam gaskets when installing the unit.
-
No instructions in the box…. Just a warranty sheet. I have completed the installation and tightened the bolts to the where the AC fan duct touches the ceiling duct. It seems to work fine.
-
40 to 50 in/lbs; pg 11
https://epi.dometic.com/externalassets/dometic-penguin-ii-13-5k-with-heat-pump_73164.pdf