Title: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 13, 2020, 08:10:43 PM
I need the collective BAC brain trust.  Coach is stored at my home plugged in to a dedicated 50A service.  Went inside yesterday and noticed everything was dead, lights were dim/not working, no incoming AC power, nothing registering on the inverter panel.  Went outside to verify pedestal breaker hadn’t tripped.  All seemed normal.  Power was still on. Turned everything off.  Started investigating today.  Verified pedestal power was good. Got in the bay and discovered that the neutral on the LOAD side of the surge guard is fried (see picture). Transfer switch looked fine.  Mine is wired: incoming AC/generator to transfer switch. Transfer switch to Surge Guard.  Surge guard to breaker panel.  Everything in breaker panel looked fine.  No burned wire.  Everything tight.  All connections at transfer switch and Surge Guard were tight.  I was in the coach about a week ago and everything was fine.  It’s stored.  There has been no significant load on the system. 

Questions: 1. I have a little l electrical experience and know dropping the neutral on a 240/120 system is no bueno.  I’m sure there is electrical component damage to electronics and what not.  Good thing is it was stored so nothing was on.  But why would the neutral over heat where it did, coming out of the surge protector.  Could there be something wrong in the surge protector?  2. Where do I go from here?  I’m not sure how far the burned wire goes up the conduit. 
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 13, 2020, 08:15:25 PM
Just realized when I viewed the pictures... when I first got to the transfer switch and SurgeGuard, power was on and feeding through to the load side of the SurgeGuard.  That’s when I turned it off at the pedestal. 
Title: Re: Electrical problem. Probably expensive.
Post by: Fred Brooks on December 13, 2020, 10:22:55 PM
    Adam,
  Picture #2 shows the origin of the short working its way into the surge protector. Note the heat deformity next to the red wire. Somewhere inside the surge protector on the load side, the red wire and the neutral got together. Seems strange under a no load condition and the green LED's all lit.
   Typically when a neutral is lost under a load, either it quits working or creates a path back to ground by way of the least resistance like a PC Board. Your insurance should cover this failure.
  To check for damage downstream of the failure, replace the damaged neutral wire (add a j-box if necessary), turn off all 120 circuit breakers. Turn on the 50amp main first, then 1 at a time and see what works. Hope this helps, Fred
PM me if you want to talk on the phone.
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 13, 2020, 10:34:37 PM
Thanks Fred.  Tomorrow I’ll peel back conduit covering the wire where the neutral is burned. See how far it goes.  I added this Surge Guard about 4 years ago.  No,issues.  Wouldn’t it be ironic if the Surge guard caused the problem!  I sent an email to Surge Guard. I’ll see what they come back with.  I pulled out a couple plugs inside that had a plug in them just to see if there was any indication of excessive heat. Everything looked good. Everything around the inverter looked good.  Charger would have been the only possible load at the time, and at most that would have been float charging. 
Title: Re: Electrical problem. Probably expensive.
Post by: Fred Brooks on December 14, 2020, 03:10:31 AM
   Adam,
I agree that there was no load and I have never seen a surge guard fail like that in 15 years. They make a quality product and as a matter of fact I have the same unit on my coach. Let me know what they say, perhaps they may want it back to analyze the internal failure. Fred
Title: Re: Electrical problem. Probably expensive.
Post by: Eric Maclean Co-Admin on December 14, 2020, 05:18:58 PM
Fred
I hate to disagree with you but the burnt neutral wire is on the load side of the unit which would lead me to believe that the burn was caused by either a loose connection at the surge protector in which case the burn should be limited to the wire with in inches of the loose connection.
If there were a short at the unit itself the neutral wire shouldn't have been involved.
If there where a short farther down stream say at the breaker panel or wiring between the surge protector and the breaker panel the hot leg which was shorted should show signs of over current as well ( insulation deformation).
At this point I'd cut the conduit open to investigate how far back the neutral is burnt if it is limited to the area close to the surge protector I'd look very closely at the neutral connection at the surge protector for discoloration and burning of the connector screw.
If the burn runs back farther follow it to the origin of the short.
Remember in our coaches there are usually are no 240 volt loads there fore all the loads weather supplied from L1 or L2 all return via that one neutral .
I would guess that the connection at the surge protector has been compromised for quite some time and that the burn happened before the coach was put in storage and as usualy happens the copper wire which has been overheated oxidizes and the connections is lost.
At any rate I would replace the surge protector and burnt neutral wire as it's been my experience that once a connection has been overheated it is impossible to get it tightened well enough to trust again.
Maybe Ed Bunker could chime in here.

Hope this helps
Eric
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 14, 2020, 05:34:15 PM
Thanks Eric.  I replaced the inverter in the spring.  At that point I checked all the connections at the transfer switch and surge guard.  Everything was snug, although I didn’t torque them.  So I know at that point all was well.  Yesterday I checked the connections and all were snug.  We had a summer of trips and all seemed fine.  It seems that a short on the load side should have tripped the main breaker, or at least the branch where the short occurred.  I’ll cut back the conduit today and see how far the burn goes. 
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 14, 2020, 06:51:08 PM
Update-  was able to peel back the wire insulation.  The neutral was damaged about 6 inches back. I’ll cut out the damage, get a new SurgeGuard.  SurgeGuard said they thought it was a loose neutral just by my description.  I sent them some pictures.  I just find it hard to believe a loose neutral was the case but I guess short of the SurgeGuard being damaged internally, that makes the most sense.  I checked all those connections in the spring.  You can never be too sure, I guess.  I’ll get it hooked back up with new parts then see what the damage is to any electronics. 🤨
Title: Re: Electrical problem. Probably expensive.
Post by: Fred Brooks on December 14, 2020, 10:33:49 PM
   Guys,
   My statements were based on the fact that I thought all the connections were torqued to spec. I should have asked that question because the entire load returns on the neutral. If the neutral was loose it would have caused the failure and the 6" burned insulation. GOOD call Eric and hopefully all turns out good! Merry Christmas! Fred
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 20, 2020, 06:27:21 PM
Another update.  I think I found the problem.  Notice in the picture there are two sets of screws on the connection block.  One set secures wires coming out of the Surge Guard.  The second set secures wires from the coach.  In this case the neutral on the SurgeGuard side was loose.  I never thought of checking that connection as it is done at the factory.  I falsely assumed it was maintenance free.  Lesson learned.  Check those connection periodically.  All of them.
Title: Re: Electrical problem. Probably expensive.
Post by: Neal E Weinmann on December 22, 2020, 05:15:22 PM
Are you certain the 34560 Surge Guard was a factory installed item? My “standard” factory installed large black TRC 40250 transfer switch has a built in Surge Guard. Perhaps a previous owner added the smaller unit as a sacrificial surge protector and did not properly torque the connections? Just wondering.
Title: Re: Electrical problem. Probably expensive.
Post by: Fred Brooks on December 23, 2020, 01:03:05 PM
    I went back thru the brochures and the 2004 Marquis showed an "optional" surge guard available. I believe Monaco started installing them shortly there after in the Beaver product line. Fred
Title: Re: Electrical problem. Probably expensive.
Post by: Neal E Weinmann on December 23, 2020, 02:54:55 PM
FWIW - if there’s a Date of Manufacture on the unit, that may help determine if it was an optional factory install or an added unit.
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 24, 2020, 06:54:27 AM
Sorry. I didn’t mean to imply that the SurgeGuard was factory installed on the coach. Only that there is a set of screws securing wires on the SurgeGuard that are factory set.  Notice in this picture, of the units side by side, that they have sealed the connections on the inner block (current model on the right) My guess is I’m not the first to have this loose connection problem. Also notice the burnt wires coming out of the device on the left top. 
Title: Re: Electrical problem. Probably expensive.
Post by: Mike Shumack on December 24, 2020, 12:29:05 PM
Why is the ground wire on the Load side (top left) so much smaller than the same wire on the Line side?



Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 25, 2020, 06:22:38 AM
Mike, I’m not exactly sure although I know a grounding wire can be one size smaller than the hot and neutral in residential wiring, but this looks to be 2 sizes smaller.  All that wiring (transfer switch included) is original coach wiring.  The wiring from the transfer switch to the load side, I added.  All wires 6awg. 
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 28, 2020, 07:10:03 AM
New update.  Installed the new SurgeGuard.  Powered everything up and much to my surprise, everything worked (almost). This is surprising because at least one outlet I tested, before I realized what was going on, had 240V.  Surprisingly, nothing fried.  All electronics work.  Microwave works.  All is normal.  Except one thing... on the Coach Monitor Panel the Leg 1 and Leg 2 voltage read “off” even though there is full voltage coming in to the coach. All other CMP functions work and are correct. 

Any ideas?
Title: Re: Electrical problem. Probably expensive.
Post by: Fred Brooks on December 28, 2020, 02:39:16 PM
   Adam,
   Where did you measure the 240 volts at. Did I understand you correctly that it was at an electrical outlet and if so was it between the neutral and the hot? The CMT gets its info from a module somewhere near the electrical breaker box not sure exactly where.
Title: Re: Electrical problem. Probably expensive.
Post by: Bill Lampkin on December 28, 2020, 05:36:06 PM
There is only one way to obtain a 230v reading on our RVs and that is to measure between two hot legs. If any receptacle measures 230v, you have a neutral crossed with a hot and you are looking at big trouble. Unplug from shore power and figure it out.
Title: Re: Electrical problem. Probably expensive.
Post by: Bill Lampkin on December 28, 2020, 06:41:27 PM
Adam, I think you have an incorrect reading when you get 230v at your outlet. if that were the case, anything plugged into that circuit would be fried. Sometimes simple is better as far as measuring AC voltage. In the trade, we used a 'Wiggy' to test for AC. Its a simple solenoid device that buzzes and lights up when AC is present. Foolproof. Here's one, there are other less pricy units out there that do the same thing.

https://www.amazon.com/Knopp-K-60-Cat-Number-14460/dp/B003A7T5KG/ref=pd_lpo_469_img_2/141-6949460-2459362?_encoding=UTF8&pd_rd_i=B003A7T5KG&pd_rd_r=4c340a2f-ea46-477a-87c5-afe13fd36552&pd_rd_w=YoVz2&pd_rd_wg=hHwz6&pf_rd_p=7b36d496-f366-4631-94d3-61b87b52511b&pf_rd_r=08HJDT5KNZ2F70BPDTZ5&psc=1&refRID=08HJDT5KNZ2F70BPDTZ5
Title: Re: Electrical problem. Probably expensive.
Post by: Joel Ashley on December 28, 2020, 11:18:32 PM
As Bill pointed out, you should only get 240 volts when one test probe is in each of the two “hot” ports.  Double check that this is the case at the park post outlet.  120v between either “hot” port and the neutral port.  Each “hot” represents a “Leg”, ie. L1 & L2.
Title: Re: Electrical problem. Probably expensive.
Post by: Adam Hicklin on December 29, 2020, 07:38:55 AM
Fred, I’ll try to take a picture of where I THINK the CMP reads the voltage. 

Bil, yes, that happened when when the SurgeGuard had a loose connection and burned up the neutral. Not exactly sure what happened internally to combine the voltage but it happened on a non-inverter circuit, so I think that’s ultimately what saved me. And nothing was plugged in to that circuit. But in all honesty, I’m not exactly sure what happened because as soon as I realized something was wrong I shut it all down and replaced the obvious failure...the SurgeGuard.
Title: Re: Electrical problem. Probably expensive.
Post by: Eric Maclean Co-Admin on December 29, 2020, 01:52:46 PM
Adam
If I understand properly you only had 240 volts at the outlets when the neutral or common wire was faulty and that with the new surge guard installed all is fine.
The reason you had 240 volts at the outlet without the neutral is that without the neutral for a return the power fed to any large low resistance load like your inverter charger or a heating element  will feed through the load to the neutral side making the neutral buss bar in the panel hot from the leg which feeds that load therefore when you checked the voltage at a receptical fed from the other leg you would effectively be reading the voltage between both incoming legs
When you restored the neutral connection the voltage at those recepticals should be back to 120 volts
I hope this is not too confusing
Hope this helps
Eric