General Boards => Technical Support => Topic started by: Joseph Garvin on March 03, 2019, 12:27:38 AM

Title: Inverter Alarm
Post by: Joseph Garvin on March 03, 2019, 12:27:38 AM
I have a FET overload Alarm on my inverter.  There is a 01 Temp.. What is a FET and what is the 01 Temp.?
Title: Re: Inverter Alarm
Post by: Mike Shumack on March 03, 2019, 12:43:05 AM
There is some info on that temp sensor in this thread. http://beaveramb.org/forum/index.php/topic,8573.msg59035.html#msg59035

That is the "Field Effect Transformer". The manual says "the higher the count, the lower the temperature".  So your (very low count) reading would indicate it is very hot (or sensor has failed). Normal on  my coach is around 213 Counts for the FET.
Title: Re: Inverter Alarm
Post by: Joseph Garvin on March 03, 2019, 01:24:40 AM
Thanks Mike. Its raining now . I will look at it in the morning.
Title: Re: Inverter Alarm
Post by: Mike Shumack on March 03, 2019, 11:12:02 AM
I recall reading something about another person with high temp alarm and in that case it was due to a faulty fan(s) inside the Inverter (but not sure if that person had a Magnum brand or Xantrex).
Perhaps you could test by setting a portable fan blowing on front of Inverter and see if the temp reading changes.
Title: Re: Inverter Alarm
Post by: Joseph Garvin on March 03, 2019, 04:36:35 PM
I'll use a fan when I get out of church.  Thanks gain.
Title: Re: Inverter Alarm
Post by: Mike Shumack on March 10, 2019, 12:11:50 AM
if your still working this issue - here is a nice YouTube video on troubleshooting the Magnum inverter.

https://www.youtube.com/watch?v=m-1OSFPHi04