Ken,
I would think that a little time inspecting would give you some insight. I would examine any hoses that could be reached with easy cover removal. Squeeze them to see if they are pliable and look for any weather checking. If they pass that test most likely tou have substantial useful life left in them. Thermostats do not fail very often so if the system is cooling well then you could take a pass on changing that item.
I would run the generator under significant load, whatever you can use in the coach to stress it a bit. After it has run for 1/2 hr to 45 minutes under load take an IR gun and shoot the radiator face, the engine block, and oil pan to get some temperature readings. Run it just enough time with the removable cover off to get the readings given that will affect cooling.
On my genset with a good belt I read 118F on the radiator face, 144F on the oil pan, and 187F high on the block. Your numbers will vary some from mine but they should be somewhat close. With a slipping belt my radiator reached 216F, oil pan 207F, and the block was 215F. You will not hear any squeal from a slipping belt in this application.
My belt failed at 350 hours at 9 years old and caused an overheat shutdown. I think your belt is in the ballpark of when it should be changed but I would check the cooling profile with an IR gun as discussed and every 3 months or so. It is good to have that data. Run the same test and change the belt when you see your cooling profile temperatures rise. Hope this helps.
Later Ed