Was in Lake Tahoe dry camping this weekend and started experiencing some problems with our inverter/charger. It is the Xantrex Freedom 20D on our 1998 Beaver Patriot.
Worked fine while simply inverting power from the batteries, however once the generator was fired up to recharge and run microwave etc for a couple hours in the mornings and nights, after about 30-40 minute of the generator running the inverter remote above the door with indicate an "overload" and shutdown.
With the generator turned off, i cycled the inverter remote off/on to reset it and it did. However it did this overload repeatedly every consecutive time the generator ran. Upon returning home today I plugged into our 50A shore power at our house and within 30-40 minutes the same thing would happen, inverter overload.
I crawled into the bay and looked at the inverter and saw nothing strange. I checked all the vents for debris and wiped them down. The inverter was extremely hot, which i'm assuming is what might likely be triggering the overload. After letting it cool down I plugged back in and the same exact thing happened within 30-40 minutes. I also listened for the sound of any fans running inside the inverter as the manual says it has cooling fans but did not hear anything obvious.
Any words of wisdom....? Or is a new inverter in my future....
Thx