Author Topic: no aqua hot in the bedroom 03 Marquis  (Read 6529 times)

william harrison

  • Guest
no aqua hot in the bedroom 03 Marquis
« on: November 07, 2016, 04:30:21 PM »
 Furnace works fine in the main living area but when I select furnace in the bedroom it blows the 10 amp fuse
that supplies power to the fans in the heat exchangers.  Using an auxiliary battery I was able
to confirm that none of the fans has a short in it; the fuse will also blow with all the fans turned off.

Steve Huber Co-Admin

  • Administrator Group
  • *
  • Posts: 3540
  • Thanked: 2720 times
Re: no aqua hot in the bedroom 03 Marquis
« Reply #1 on: November 07, 2016, 06:15:05 PM »
William,
Need a bit more info (at least I do). Where is 10 amp fuse located? When using a battery, how did you hook it to the fan circuit; at each fan with the original leads disconnected or at the fan switch leads, or? The fuse blows when all fans are off but what is on. What do you turn on to make the fuse blow with the fans off?
Thx, Steve
Steve
Coachless
2015- 6/24  07 Contessa Bayshore C9,  400 hp
2013-2015: 00 Marquis Tourmaline, C12, 425 hp
2005-2013: 01 Contessa Naples, 3126B, 330 hp

Gerald Farris

  • Guest
Re: no aqua hot in the bedroom 03 Marquis
« Reply #2 on: November 08, 2016, 01:10:15 PM »
William,
Since the AquaHot system uses a circulation pump for each zone, you may have a shorted circulation pump or at least that is the next thing that I would check.

Gerald

Orman Claxton

  • Guest
Re: no aqua hot in the bedroom 03 Marquis
« Reply #3 on: November 11, 2016, 04:07:23 AM »
Hi William
Give me a call, I see if I can c talk you through some trouble shooting

Fred Brooks

  • BAC Member
  • *
  • Posts: 1617
  • Thanked: 749 times
  • RVIA Certified Luxury Technician 49 years, Retired
Re: no aqua hot in the bedroom 03 Marquis
« Reply #4 on: November 11, 2016, 01:26:37 PM »
     Hi William,
   I agree with Gerald. If you can access the service area of your Aqua-Hot, try unplugging the zone pumps one at a time to see if the fuse stops blowing. If not then the issue may be in a shorted wire somewhere between the heat exchanger and the aqua-hot
  Regards, Fred
Fred & Cindy Brooks
2000 Marquis, Jasper
C-12 Wild Cat (U of A)
2014 Honda CRV
Proverbs 3: 5 & 6

Orman Claxton

  • Guest
Re: no aqua hot in the bedroom 03 Marquis
« Reply #5 on: November 15, 2016, 06:29:56 PM »
OR Maybe a stuck check valve

Rhonda Price

  • Guest
Hydro hot furnace in bedroom does not work 2006 beaver monterey
« Reply #6 on: November 08, 2017, 05:17:42 PM »
Where can we find  to check for a stuck check valve for the furnace that is not blowing heat in the bedroom only cool air living rm works

Steve Huber Co-Admin

  • Administrator Group
  • *
  • Posts: 3540
  • Thanked: 2720 times
Re: no aqua hot in the bedroom 03 Marquis
« Reply #7 on: November 08, 2017, 06:27:58 PM »
Sounds like a zone pump might not be working. You can remove the AH cover and see if the pumps are running. Also check to see if you have a fault indicator  for a pump on the electronic controller panel. The bedroom is probably zone 2 or 3 depending on your AH model. Thermostat is probably OK if fan is running on bedroom heat exchanger.
Steve
« Last Edit: November 08, 2017, 07:37:53 PM by Steve Huber Co-Admin »
Steve
Coachless
2015- 6/24  07 Contessa Bayshore C9,  400 hp
2013-2015: 00 Marquis Tourmaline, C12, 425 hp
2005-2013: 01 Contessa Naples, 3126B, 330 hp

Bill Sprague

  • Guest
Re: no aqua hot in the bedroom 03 Marquis
« Reply #8 on: November 09, 2017, 02:09:29 AM »
It is not uncommon for the check valves to stick shut when not in use for awhile.  Firmly tapping on them gets them working again.  The check valves should be easy to find.

Steve Huber Co-Admin

  • Administrator Group
  • *
  • Posts: 3540
  • Thanked: 2720 times
Re: no aqua hot in the bedroom 03 Marquis
« Reply #9 on: November 09, 2017, 02:24:56 AM »
You can find the parts locator in the service manual for your specific unit.   http://www.aquahot.com/Library.aspx
Steve
Steve
Coachless
2015- 6/24  07 Contessa Bayshore C9,  400 hp
2013-2015: 00 Marquis Tourmaline, C12, 425 hp
2005-2013: 01 Contessa Naples, 3126B, 330 hp
The following users thanked this post: Mike Sulley

Bill Lampkin

  • BAC Member
  • *
  • Posts: 1234
  • Thanked: 360 times
Re: no aqua hot in the bedroom 03 Marquis
« Reply #10 on: November 10, 2017, 06:46:14 PM »
a centrifugal pump (zone pump) pulls power in proportion to the amount of fluid moving through the pump, i.e., if the check valve is stuck closed, the pump is not pumping fluid and will not have an increase in the amount of current it draws, should not blow a fuse (current) if the check valve is stuck.