Our coach has been parked here by the house for a number of years, unused due to sequential health issues.  I try to run the genset and the HydroHot for 20-30 mins every 2 to 4 months.  The genset runs well and I load it with a small infrared oven in the galley that handily cycles on and off.

Today was another very hot one.  But the wind finally kicked up enough for once to help clear exhaust smoke away from the proximal fence, so the neighbors aren’t asphyxiated.  In this community of 6000-10,000 sf. lots, I can imagine getting complaints;  as an asthmatic I’m sensitive myself.   Their windows apparently shut due to the heat, I ran the two devices.  But for the 3rd or 5th time the HydroHot’s exhaust was pretty smoky again, and didn’t clear up much over twenty minutes.   The cedar fence, 3 ft. away from the exhaust pipe, darkened a bit with soot.  I watched in aggravation as grayness drifted up the fence face, but then mercifully got caught by the wind and wafted over the coach and away.   I’d hate to think of running the hydronics in a campground  :-\  if we actually managed to get on the road again soon as hoped.

With a relatively long pipe, soot buildup may be part of the problem.  Or it’s just running rich.  Before digging into the troubleshooting part of the manual, is there a simple adjustment I can make in the burner mix to help ameliorate the smoking?   The vent pipe through the bay floor appears clear from the outside, but I haven’t had the shroud off the unit since replacing the tank level sensor a few years ago.

Joel
Joel and Lee Rae Ashley
Clackamas, Oregon
36.9 ft. 2006 Monterey Ventura IV, aka"Monty Rae"
C9 400HP Cat

Eric Maclean

  • BAC Member
  • *
  • Posts: 1227
  • Thanked: 453 times
  • Karen and I would like to wish you all happy trail
Re: Smokin’ hot
« Reply #1 on: August 25, 2023, 02:37:14 PM »
Joel the hydrohot just like the aquahot requires enough air flow through the unit to get complete combustion .
There are several things that could cause your rich operation
1) burner nozzle ( dirt or poor atomization,improper spray pattern)
2) low voltage condition causing slower blower speeds and not enough air movement
3) blower bearings dragging again causing lower blower speeds
4) exhaust pipe particle blockage ( rust and soot buildup causing poor air flow through combustion chamber)
5) air leaks around the burner head at the combustion chamber ( grommets on the electrical and fuel passthroughs )
6) melted down combustion chamber air swirler causing poor air flow and incomplete burn

I would start with a good service
1) remove the burner head
2) inspect the combustion chamber tube for cracks and the swirler for signs of aluminum melting down
3) clean the combustion chamber with a wire brush to remove soot buildup
4) using a fish tape pull a small rope through the exhaust pipe from the combustion chamber to the tail pipe tie a rage to it and pull it back a d forth to clean and verify the exhaust is clear
5) remove the rear black plastic cover from the burner head and spin the motor by hand listen for bearing noise in the blower housing
6) if you have an optical tachometer power up the motor with 12 volts and measure the shaft speed at the coupler this should be done with the fuel pump drawing fuel for the proper load the spec is 4500 RPM +/- 300 however every one I've tested has been in the 5000 RPM range.
7) if you have a fuel pressure gauge to screw into the nozzle opening check fuel pressure as described in the manual the spec is 145 PSI and is adjustable on the side of the pump
8) replace the rear cover
9) replace the burner nozzle with a new 0.35 gph 60* nozzle
10) reinstall the burner tube the seam in the tube must face up 12 o'clock position
11) reinstall the burner head
12) cycle the burner and check for any air escaping around the burner ( grommets and combustion chamber) no leakage is acceptable

Finally to answer your question yes there is an air adjustment aperture on the air intake this is there officially to allow CO adjustment but as you move to higher elevation it needs to be opened up to make up for the thinker air density.

Remember if the unit has been flooded ( too much fuel ) there will be a buildup in the exhaust which will take several cycles to clear before the unit will run clean therefore I don't recommend making any air adjustments until the unit has been serviced and run for a period of time to clear itself before making the air adjustment.
There is a screw on the aperture usually at the right side of the intake tube loosen the screw and move the screw in the slotted whole towards the combustion chamber will increase the air flow ( leaner)and pulling it back towards you will decrease the air flow ( richer)
Before moving it take a paint pen and index the screw for future reference.

Hope this helps
Eric
1997 Patriot Yorktown
3126-B
2009 Chevy HHR
Roadmaster falcon tow bar
Demco Air Force one tow brake.
The following users thanked this post: Joel Ashley

Steve Huber Co-Admin

  • Administrator Group
  • *
  • Posts: 3538
  • Thanked: 2719 times
Re: Smokin’ hot
« Reply #2 on: August 25, 2023, 03:16:23 PM »
Joel,
IMHO there is no need to run the HH monthly if you aren't using it. I normally use the electric service when traveling as the engine heat will keep water hot and the geni will keep it running overnight since we use the A/Cs. I checked with AH factory tech and confirmed there was no issue in not running diesel for long periods of time. I run mine about 1/year minimum.
Steve