We have an issue where our 50 amp breaker is randomly tripping when all 3 A/C units are running.  I have shut off all of the other things that I can think of that might be adding to the amp total.  The refer and the TV are still on.

What is the chance that the breaker has gotten weak?

David T. Richelderfer

  • David, Leslie, Jasper, & JoJo
  • BAC Member
  • *
  • Posts: 1688
  • Thanked: 498 times
  • OSU, Class of 1971, RVing nearly 50 years
Re: 50 AMP BREAKER TRIPPING
« Reply #1 on: June 26, 2018, 03:31:30 PM »
While on shore power or generator?
Generator size?
Breaker on one of two 50a legs trips?
       Always the breaker on the leg with two a/c's that trips?
Is it possible one a/c has gone bad?  (I had one of three a/c's go bad and on startup it would pull 75a+ due to a bad bearing.)
Where are your 50a breakers located?  (I don't have 50a breakers, do I?  Maybe in the generator?  I must look. lol)
2004 Beaver Marquis Sapphire

I had a dream... then I lived it!

Bill Staley

  • Guest
Re: 50 AMP BREAKER TRIPPING
« Reply #2 on: June 26, 2018, 05:04:29 PM »
They trip while on shore power. 
I just had them ( all three) checked so there shouldn't be a startup problem.
Dual breakers.
And, each A/C has their own breaker.
Only the 50A trips.
The breakers are located in the AC panel in the bathroom.
I really don't think it is the A/C units that are causing the problem.  Am wondering if others need to shut down one of the A/C units whit they run other appliances.

Bill Sprague

  • Guest
Re: 50 AMP BREAKER TRIPPING
« Reply #3 on: June 26, 2018, 05:40:20 PM »
You have a pair of 50 amp breakers, for 100 total.  It is a two leg system.  The right column of breakers is one leg and the left column the other.  Because you have three A/C units, two will be on one side and one will be on the other. 

Each A/C will draw about 13 AMPs with peaks to about 20 as the compressor cycles.  What else is on the leg that has two A/Cs on it?

Can you tell which of the two 50 amp breakers is tripping?  Can you monitor loads on your Aladin screen?