Hey guys, I hate to be a pain but I have a question about hooking up a 50 amp service. OK, first off I already have a 50 amp service to our Hot Tub. We're going to be taking that out, and I'm going to use the existing wiring to run to an RV hookup. I'll just use a 4x4 gang box form the Hot Tub area over to the RV hookup. Total run is around 65ft. I have #6 wire now, and that should work. Now, here's what I did when I originally ran the wiring. I ran the white(neutral) as #12, thinking it was not a load carrying wire. It's worked out OK tho. But what I'm thinking is I prob need to pull that #12 out(it's run under ground in conduit) and replace it with at least #10...or if I'm doing all that work, I might as well use #6. I think I read somewhere that the white needs to be able to carry 70% of the rated load which would be around 35 amps(which would be at least a #10). Is that right? Or am I OK with keeping the #12 as the neutral(prob not)? Thanks in advance for any help.