The recent problems we had with the main power transfer relay and the power transfer relay within the Xantrex forced me to take a closer look at how all of the circuitry is tied together.
Here are some of my conclusions:
The Xantrex remote panel can only monitor or impact the circuits which are tied thru the inverter converter, not all circuits into the coach. Therefore the only values which may actually impact current flow thru the inverter/converter are the 5A, 15A and 20A settings. All other settings will assume full power to the inverter/converter and achieve the same results. The Xantrex remote panel which displays the various voltage settings for limiting input voltage is slaved off the Xantrex inverter/converter. Shore power is actually wired thru the 50 amp power transfer relay first. That power transfer relay is intended to provide service either via shore power or the genset. From the primary power transfer relay, the house wiring is connected to the 50 amp panel in the coach. The 30 amp inverter is actually slaved to the 50 amp panel thru a 30 amp breaker. The AC output leg of the Xantrex inverter ties to 3 separate AC circuits which feed most of the GFCI circuits in the coach, the AC lights, Bose sound system, and the AC side of the Fantastic vents used to run the fan motors.
The remaining major appliances (air conditioning units, washer dryer, water heater circuits, refrigerator and a single outlet in the dining area) are all on their own circuit breakers and not tied thru the Xantrex inverter/converter. Therefore, current flow to those circuits is not impacted by any settings on the Xantrex remote.
The power transfer relay in the Xantrex is used to switch between the external AC input and the inverter. The interesting thing about the Xantrex power transfer relay is that it is designed to support two separate 30 amp inputs and feed two separate AC output legs. In our 2000 Patriot Thunder coach there is only one input and one output leg used. If and/ or when we encounter another Xantrex failure I will rewire to circuit 2. This action assumes the problem is due to pitted contacts on the power transfer relay If that doesn’t resolve the issue the next step would be to replace the power relay (Deltrol Controls 375TM 3PDT) or as a last resort take the inverter/converter to an authorized Xantrex service center and spend the $350 for the AC circuit board + labor for removal and re-installation.
Hope this helps anyone else dealing with these problems.